Old 02-27-2021, 12:14pm   #1
Aerovette
Chief Electrician
Barn Stall Owner #7734

Bantayan Kids '15
Points: 104,911, Level: 100
Activity: 99.2%
 
Aerovette's Avatar
 
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 43,838
Thanks: 16,804
Thanked 33,376 Times in 13,464 Posts
Gameroom Barn Bucks: $107478
Default Electrical issue HVAC

This has been going oin for two years.

My AC works fine and heater works fine. The issue is the transition from one to the other. If I run the AC during the day and switch to heat, all is well. If I switch from heat to AC, the outside unit trips the breaker. If I try to flip the breaker on, it just trips again. The only way I can go from heat to AC, is to turn the system OFF, flip the breaker on, then turn the system back on. So strange. Once I do this ONE TIME, the AC will cycle just fine every time. If I run the heater again, I have to repeat these steps.

Heater cycles fine
AC cycles fine
AC to heat, works fine
Heat to AC trips the breaker
Shut down, set breaker, restart...all good.
Aerovette is offline   Reply With Quote
Old 02-27-2021, 12:22pm   #2
ZipZap
Barn Stall Owner #55
Island14 Cardio Team
Points: 62,628, Level: 100
Activity: 92.4%
 
ZipZap's Avatar
 
Join Date: Jan 2011
Location: A sympathetic, well-meaning, elderly man with a poor memory
Posts: 14,663
Thanks: 3,732
Thanked 9,142 Times in 4,337 Posts
Gameroom Barn Bucks: $23236
Default

How old is the breaker? I have had them wear out.
ZipZap is offline   Reply With Quote
Old 02-27-2021, 12:30pm   #3
Aerovette
Chief Electrician
Barn Stall Owner #7734

Bantayan Kids '15
Points: 104,911, Level: 100
Activity: 99.2%
 
Aerovette's Avatar
 
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 43,838
Thanks: 16,804
Thanked 33,376 Times in 13,464 Posts
Gameroom Barn Bucks: $107478
Default

Quote:
Originally Posted by ZipZap View Post
How old is the breaker? I have had them wear out.
Every breaker in the house is 14 years old. Why is it that is cycles just fine? Inrush current is the same at cycling as it is a start up.
Aerovette is offline   Reply With Quote
Old 02-27-2021, 12:41pm   #4
ZipZap
Barn Stall Owner #55
Island14 Cardio Team
Points: 62,628, Level: 100
Activity: 92.4%
 
ZipZap's Avatar
 
Join Date: Jan 2011
Location: A sympathetic, well-meaning, elderly man with a poor memory
Posts: 14,663
Thanks: 3,732
Thanked 9,142 Times in 4,337 Posts
Gameroom Barn Bucks: $23236
Default

Quote:
Originally Posted by aerovette View Post
Every breaker in the house is 14 years old. Why is it that is cycles just fine? Inrush current is the same at cycling as it is a start up.
Inrush clearly is not the same if it's tripping. Is there current from the heater still on the circuit that's not there when you do a recycle? Do you have flue dampers? The only other thing that I can think of is an issue with the HVAC itself. How does the capacitor look?
ZipZap is offline   Reply With Quote
Old 02-27-2021, 12:51pm   #5
Aerovette
Chief Electrician
Barn Stall Owner #7734

Bantayan Kids '15
Points: 104,911, Level: 100
Activity: 99.2%
 
Aerovette's Avatar
 
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 43,838
Thanks: 16,804
Thanked 33,376 Times in 13,464 Posts
Gameroom Barn Bucks: $107478
Default

Quote:
Originally Posted by ZipZap View Post
Inrush clearly is not the same if it's tripping. Is there current from the heater still on the circuit that's not there when you do a recycle? Do you have flue dampers? The only other thing that I can think of is an issue with the HVAC itself. How does the capacitor look?
Capacitor is new-ish. Replaced last year. The start up process kicks on the blower, outside fan, and compressor. The cycle process kicks on the blower, outside fan, and the compressor. What else could be in the circuit in one case, that is not there in the other? Also, it is a gas heater.
Aerovette is offline   Reply With Quote
Old 02-27-2021, 1:18pm   #6
BayouCountry
Barn Stall Owner #105
Points: 5,255, Level: 49
Activity: 14.0%
 
BayouCountry's Avatar
 
Join Date: Jan 2021
Posts: 1,182
Thanks: 205
Thanked 1,351 Times in 584 Posts
Gameroom Barn Bucks: $500
Default

Replace breaker if resetting service power switch doesn't work.

What happens if you reset the air handler breaker after turning off heat?
What happens if you reset the outside service switch after turning off the heat?

You didn't mention if the condenser has a heat pump.
BayouCountry is offline   Reply With Quote
Old 02-27-2021, 1:23pm   #7
VatorMan
Barn Stall Owner #122
NCM Supporter '11,'13
Bantayan Kids '13,'14,'17
Points: 68,055, Level: 100
Activity: 11.2%
 
VatorMan's Avatar
 
Join Date: Oct 2009
Location: Gaithersburg, MD.
Posts: 22,499
Thanks: 6,154
Thanked 8,380 Times in 4,242 Posts
Gameroom Barn Bucks: $1158963
Default

I just had the breaker to my heat pump give up the ghost. Breakers get weak over the years. Takes less to make them trip.
VatorMan is offline   Reply With Quote
The Following User Says Thank You to VatorMan For This Useful Post:
Old 02-27-2021, 2:00pm   #8
Aerovette
Chief Electrician
Barn Stall Owner #7734

Bantayan Kids '15
Points: 104,911, Level: 100
Activity: 99.2%
 
Aerovette's Avatar
 
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 43,838
Thanks: 16,804
Thanked 33,376 Times in 13,464 Posts
Gameroom Barn Bucks: $107478
Default

Quote:
Originally Posted by BayouCountry View Post
Replace breaker if resetting service power switch doesn't work.

What happens if you reset the air handler breaker after turning off heat?
What happens if you reset the outside service switch after turning off the heat?

You didn't mention if the condenser has a heat pump.

No heat pump. No issue during heat or switch from AC to heat. Only heat to AC. For AC to heat, all I do is set the thermostat to heat and set the temp. If I do this going from heat to AC, the t-stat kicks the inside blower on, but the outside unit breaker trips. If I try to reset the breaker with the unit on AC and blower running, it will never reset. I have to turn the t-stat to "off", reset the breaker, then go back to the t-stat, set to "cool"and set the temp.
Aerovette is offline   Reply With Quote
Old 02-27-2021, 2:20pm   #9
mrvette
Latin American Goat Roper
Barn Stall Owner #101
Bantayan Kids '13
Points: 132,350, Level: 100
Activity: 10.8%
 
mrvette's Avatar
 
Join Date: Nov 2009
Location: Orange Park Florida
Posts: 60,580
Thanks: 32,796
Thanked 11,529 Times in 5,686 Posts
Gameroom Barn Bucks: $1138393
Default

Head pressure in the coils, too much for comp to restart quickly into operating head pressures.....sounds to ME, there was a delay circuit in the control/stat? somehow to stop that, and it's not doing the job....allows outside comp to come on too fast.....

Y R U changing back/forth anyway??? we run overnight heat at say 72f in the house.....and we been opening windoze during the day.....except today it's much higher outside, but house is cool indoors yet, bright sunny day and over 90f in the atrium, but still only 72 in the house.....
mrvette is offline   Reply With Quote
Old 02-27-2021, 2:29pm   #10
bill_daniels
10cm member
Barn Stall Owner #90125

NCM Supporter '19,'20
Points: 219,842, Level: 100
Activity: 99.4%
 
bill_daniels's Avatar
 
Join Date: Jan 2011
Location: Houston, Tejas, Estados Unidos
Posts: 80,865
Thanks: 36,574
Thanked 41,061 Times in 17,072 Posts
Gameroom Barn Bucks: $2621492
Default

I concur with the folks saying it sounds like a weak breaker in your control panel. Having said that, I wonder if installing one of those "hard start" units on your ac's would help? That would be treating the symptom, probably not the cause.

And also, I agree with Gene. I don't think I've ever used the a/c and heat together in the same day. Then again, for me, cheapness overshadows comfort. I would feel bad about paying to change the temperature I already paid to regulate the other way.

I also do the same thing Gene does, when it's temperate outside and not too humid, I'll open up some windows and just kind of ventilate the house. I do the same thing in May, when it's cool at night but hot in the day. I like to get the cool night air into the house, then shut the windows in the morning and capture the coolness, as it were. Makes it easier on the a/c.
bill_daniels is offline   Reply With Quote
The Following User Says Thank You to bill_daniels For This Useful Post:
Old 02-27-2021, 2:36pm   #11
Aerovette
Chief Electrician
Barn Stall Owner #7734

Bantayan Kids '15
Points: 104,911, Level: 100
Activity: 99.2%
 
Aerovette's Avatar
 
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 43,838
Thanks: 16,804
Thanked 33,376 Times in 13,464 Posts
Gameroom Barn Bucks: $107478
Default

Quote:
Originally Posted by mrvette View Post
Head pressure in the coils, too much for comp to restart quickly into operating head pressures.....sounds to ME, there was a delay circuit in the control/stat? somehow to stop that, and it's not doing the job....allows outside comp to come on too fast.....

Y R U changing back/forth anyway??? we run overnight heat at say 72f in the house.....and we been opening windoze during the day.....except today it's much higher outside, but house is cool indoors yet, bright sunny day and over 90f in the atrium, but still only 72 in the house.....
Mid 60s at night and 80s in the day. I have a central unit to provide comfort at both times. That's what it's there for.

Why would the head pressure be high after sitting inoperable all night? Also turning the system off and setting the breaker, doesn't change the head pressure.
Aerovette is offline   Reply With Quote
Old 02-27-2021, 3:06pm   #12
Vandelay Industries
Barn Stall Owner #14/32
Points: 37,766, Level: 100
Activity: 58.6%
 
Vandelay Industries's Avatar
 
Join Date: Jan 2020
Location: IDK, IDC, IDGAF
Posts: 21,207
Thanks: 14,296
Thanked 12,914 Times in 4,897 Posts
Gameroom Barn Bucks: $4810
Default

Time to call an electrician.






























Vandelay Industries is offline   Reply With Quote
The Following 2 Users Say Thank You to Vandelay Industries For This Useful Post:
Old 02-27-2021, 3:49pm   #13
Stevedore
Bantayan Kids '17
Points: 15,089, Level: 84
Activity: 1.1%
 
Stevedore's Avatar
 
Join Date: Mar 2014
Location: Long Valley, NJ
Posts: 2,464
Thanks: 1,113
Thanked 996 Times in 529 Posts
Gameroom Barn Bucks: $406058
Default

Is the condensing unit (outside) the only thing on the problem breaker circuit? (as it should be)
Stevedore is offline   Reply With Quote
Old 02-27-2021, 3:54pm   #14
Aerovette
Chief Electrician
Barn Stall Owner #7734

Bantayan Kids '15
Points: 104,911, Level: 100
Activity: 99.2%
 
Aerovette's Avatar
 
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 43,838
Thanks: 16,804
Thanked 33,376 Times in 13,464 Posts
Gameroom Barn Bucks: $107478
Default

Quote:
Originally Posted by Stevedore View Post
Is the condensing unit (outside) the only thing on the problem breaker circuit? (as it should be)
Yes.
Aerovette is offline   Reply With Quote
Old 02-27-2021, 6:16pm   #15
mrvette
Latin American Goat Roper
Barn Stall Owner #101
Bantayan Kids '13
Points: 132,350, Level: 100
Activity: 10.8%
 
mrvette's Avatar
 
Join Date: Nov 2009
Location: Orange Park Florida
Posts: 60,580
Thanks: 32,796
Thanked 11,529 Times in 5,686 Posts
Gameroom Barn Bucks: $1138393
Default

Quote:
Originally Posted by aerovette View Post
Mid 60s at night and 80s in the day. I have a central unit to provide comfort at both times. That's what it's there for.

Why would the head pressure be high after sitting inoperable all night? Also turning the system off and setting the breaker, doesn't change the head pressure.
I had thought you going from Heat to A/C or reverse.....and so doing it quickly wood trip up.......

but if NOT, and the system is relaxed before changeout......I DUNNO....



BUTT there is one last guess......you have some gas flow valve that is not working right.....Y is another guess.....
mrvette is offline   Reply With Quote
Old 02-27-2021, 6:47pm   #16
Rodnok1
A Real Barner
Points: 41,806, Level: 100
Activity: 63.3%
 
Rodnok1's Avatar
 
Join Date: Apr 2019
Location: North Carolina
Posts: 16,988
Thanks: 4,837
Thanked 23,712 Times in 9,798 Posts
Gameroom Barn Bucks: $315482
Default

If it cycles fine without popping breaker i doubt it's the breaker, almost sounds like furnace/thermo is sending wrong signal to me. It may be setup(thermo) as a heat pump instead of separate untis.
Migh t want to check model of thermostat and make sure it's compatible.
Rodnok1 is offline   Reply With Quote
Reply

The Vette Barn > Off Topic/Babes/Other > Off Topic


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 4:26am.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.
Copyright © 2009 - 2024 The Vette Barn


Support the Barn:
 
Download the Mobile App;
 
Follow us on Facebook:

Become a Stall Owner

 

Apple iOS App        Google Android App

 

Visit our Facebook page