Electrical issue HVAC
This has been going oin for two years.
My AC works fine and heater works fine. The issue is the transition from one to the other. If I run the AC during the day and switch to heat, all is well. If I switch from heat to AC, the outside unit trips the breaker. If I try to flip the breaker on, it just trips again. The only way I can go from heat to AC, is to turn the system OFF, flip the breaker on, then turn the system back on. So strange. Once I do this ONE TIME, the AC will cycle just fine every time. If I run the heater again, I have to repeat these steps. Heater cycles fine AC cycles fine AC to heat, works fine Heat to AC trips the breaker Shut down, set breaker, restart...all good. |
||||||
02-27-2021, 12:22pm | #2 | ||||||
Barn Stall Owner #55
Island14 Cardio Team
Join Date: Jan 2011
Location: A sympathetic, well-meaning, elderly man with a poor memory
Posts: 14,735
Thanks: 3,746
Thanked 9,186 Times in 4,360 Posts
Gameroom Barn Bucks: $23236
|
How old is the breaker? I have had them wear out.
|
||||||
02-27-2021, 12:30pm | #3 | ||||||
Chief Electrician
Barn Stall Owner #7734 Bantayan Kids '15
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 44,277
Thanks: 16,984
Thanked 33,597 Times in 13,594 Posts
Gameroom Barn Bucks: $107478
|
|
||||||
02-27-2021, 12:41pm | #4 | ||||||
Barn Stall Owner #55
Island14 Cardio Team
Join Date: Jan 2011
Location: A sympathetic, well-meaning, elderly man with a poor memory
Posts: 14,735
Thanks: 3,746
Thanked 9,186 Times in 4,360 Posts
Gameroom Barn Bucks: $23236
|
Inrush clearly is not the same if it's tripping. Is there current from the heater still on the circuit that's not there when you do a recycle? Do you have flue dampers? The only other thing that I can think of is an issue with the HVAC itself. How does the capacitor look?
|
||||||
02-27-2021, 12:51pm | #5 | |||||||
Chief Electrician
Barn Stall Owner #7734 Bantayan Kids '15
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 44,277
Thanks: 16,984
Thanked 33,597 Times in 13,594 Posts
Gameroom Barn Bucks: $107478
|
Quote:
|
|||||||
02-27-2021, 1:18pm | #6 | ||||||
Barn Stall Owner #105
Join Date: Jan 2021
Posts: 1,205
Thanks: 207
Thanked 1,363 Times in 591 Posts
Gameroom Barn Bucks: $500
|
Replace breaker if resetting service power switch doesn't work.
What happens if you reset the air handler breaker after turning off heat? What happens if you reset the outside service switch after turning off the heat? You didn't mention if the condenser has a heat pump. |
||||||
02-27-2021, 1:23pm | #7 | ||||||
Barn Stall Owner #122
NCM Supporter '11,'13 Bantayan Kids '13,'14,'17
Join Date: Oct 2009
Location: Gaithersburg, MD.
Posts: 22,543
Thanks: 6,175
Thanked 8,398 Times in 4,251 Posts
Gameroom Barn Bucks: $1158963
|
I just had the breaker to my heat pump give up the ghost. Breakers get weak over the years. Takes less to make them trip.
|
||||||
The Following User Says Thank You to VatorMan For This Useful Post: |
02-27-2021, 2:00pm | #8 | |||||||
Chief Electrician
Barn Stall Owner #7734 Bantayan Kids '15
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 44,277
Thanks: 16,984
Thanked 33,597 Times in 13,594 Posts
Gameroom Barn Bucks: $107478
|
Quote:
No heat pump. No issue during heat or switch from AC to heat. Only heat to AC. For AC to heat, all I do is set the thermostat to heat and set the temp. If I do this going from heat to AC, the t-stat kicks the inside blower on, but the outside unit breaker trips. If I try to reset the breaker with the unit on AC and blower running, it will never reset. I have to turn the t-stat to "off", reset the breaker, then go back to the t-stat, set to "cool"and set the temp. |
|||||||
02-27-2021, 2:20pm | #9 | ||||||
Latin American Goat Roper
Barn Stall Owner #101 Bantayan Kids '13
Join Date: Nov 2009
Location: Orange Park Florida
Posts: 60,678
Thanks: 32,872
Thanked 11,544 Times in 5,694 Posts
Gameroom Barn Bucks: $1138393
|
Head pressure in the coils, too much for comp to restart quickly into operating head pressures.....sounds to ME, there was a delay circuit in the control/stat? somehow to stop that, and it's not doing the job....allows outside comp to come on too fast.....
Y R U changing back/forth anyway??? we run overnight heat at say 72f in the house.....and we been opening windoze during the day.....except today it's much higher outside, but house is cool indoors yet, bright sunny day and over 90f in the atrium, but still only 72 in the house..... |
||||||
02-27-2021, 2:29pm | #10 | ||||||
10cm member
Barn Stall Owner #90125 NCM Supporter '19,'20
Join Date: Jan 2011
Location: Houston, Tejas, Estados Unidos
Posts: 81,439
Thanks: 36,923
Thanked 41,249 Times in 17,152 Posts
Gameroom Barn Bucks: $2621492
|
I concur with the folks saying it sounds like a weak breaker in your control panel. Having said that, I wonder if installing one of those "hard start" units on your ac's would help? That would be treating the symptom, probably not the cause.
And also, I agree with Gene. I don't think I've ever used the a/c and heat together in the same day. Then again, for me, cheapness overshadows comfort. I would feel bad about paying to change the temperature I already paid to regulate the other way. I also do the same thing Gene does, when it's temperate outside and not too humid, I'll open up some windows and just kind of ventilate the house. I do the same thing in May, when it's cool at night but hot in the day. I like to get the cool night air into the house, then shut the windows in the morning and capture the coolness, as it were. Makes it easier on the a/c. |
||||||
The Following User Says Thank You to bill_daniels For This Useful Post: |
02-27-2021, 2:36pm | #11 | |||||||
Chief Electrician
Barn Stall Owner #7734 Bantayan Kids '15
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 44,277
Thanks: 16,984
Thanked 33,597 Times in 13,594 Posts
Gameroom Barn Bucks: $107478
|
Quote:
Why would the head pressure be high after sitting inoperable all night? Also turning the system off and setting the breaker, doesn't change the head pressure. |
|||||||
02-27-2021, 3:06pm | #12 | ||||||
Barn Stall Owner #14/32
Join Date: Jan 2020
Location: IDK, IDC, IDGAF
Posts: 21,335
Thanks: 14,361
Thanked 13,003 Times in 4,934 Posts
Gameroom Barn Bucks: $4810
|
Time to call an electrician.
|
||||||
The Following 2 Users Say Thank You to Vandelay Industries For This Useful Post: |
02-27-2021, 3:49pm | #13 | ||||||
Bantayan Kids '17
Join Date: Mar 2014
Location: Long Valley, NJ
Posts: 2,470
Thanks: 1,116
Thanked 996 Times in 529 Posts
Gameroom Barn Bucks: $406058
|
Is the condensing unit (outside) the only thing on the problem breaker circuit? (as it should be)
|
||||||
02-27-2021, 3:54pm | #14 | ||||||
Chief Electrician
Barn Stall Owner #7734 Bantayan Kids '15
Join Date: Jan 2011
Location: The corner of Cease Rd. and Desist St.
Posts: 44,277
Thanks: 16,984
Thanked 33,597 Times in 13,594 Posts
Gameroom Barn Bucks: $107478
|
|
||||||
02-27-2021, 6:16pm | #15 | |||||||
Latin American Goat Roper
Barn Stall Owner #101 Bantayan Kids '13
Join Date: Nov 2009
Location: Orange Park Florida
Posts: 60,678
Thanks: 32,872
Thanked 11,544 Times in 5,694 Posts
Gameroom Barn Bucks: $1138393
|
Quote:
but if NOT, and the system is relaxed before changeout......I DUNNO.... BUTT there is one last guess......you have some gas flow valve that is not working right.....Y is another guess..... |
|||||||
02-27-2021, 6:47pm | #16 | ||||||
A Real Barner
Join Date: Apr 2019
Location: North Carolina
Posts: 17,213
Thanks: 4,902
Thanked 23,880 Times in 9,907 Posts
Gameroom Barn Bucks: $315482
|
If it cycles fine without popping breaker i doubt it's the breaker, almost sounds like furnace/thermo is sending wrong signal to me. It may be setup(thermo) as a heat pump instead of separate untis.
Migh t want to check model of thermostat and make sure it's compatible. |
||||||