Default Any electrical experts here - Variacs and GFCI's

I have a code issue at work that I am having difficulty getting a clear answer on. We have numerous variable auto-transformers (variacs) that are within the range where GFCI is required. These are relatively new in age so the GFCi requirements were in place at the time of installation and of course the manufacturer is no longer in business.

I have read various reasons whey they are not GFCI - GFCI is ineffective below 100 volts, GFCi will trip due to being too sensitivity incompatibilities, etc. Has anyone had any experience with this that could shed light on to why these were not connected to GFCI originally, otherwise I may need to setup a test area
Attached Thumbnails
IMG_9997.jpg  

Black94lt1 is offline   Reply With Quote
Old 07-10-2019, 4:57pm   #2
ZipZap
Barn Stall Owner #55
Island14 Cardio Team
Points: 61,734, Level: 100
Activity: 94.2%
 
ZipZap's Avatar
 
Join Date: Jan 2011
Location: A sympathetic, well-meaning, elderly man with a poor memory
Posts: 14,514
Thanks: 3,700
Thanked 9,066 Times in 4,289 Posts
Gameroom Barn Bucks: $23236
Default

I'm assuming this is a non-isolated VAT. Could you run an isolation transformer upstream and then use a GFCI?

Or, are you trying to GFCI the output?
ZipZap is online now   Reply With Quote
Old 07-10-2019, 5:54pm   #3
mrvette
Latin American Goat Roper
Barn Stall Owner #101
Bantayan Kids '13
Points: 132,054, Level: 100
Activity: 12.9%
 
mrvette's Avatar
 
Join Date: Nov 2009
Location: Orange Park Florida
Posts: 60,529
Thanks: 32,757
Thanked 11,510 Times in 5,682 Posts
Gameroom Barn Bucks: $1138393
Default

Any properly wired Variac should not upset a decent GFCI breaker.....

now, turning it on/off with a power switch MAY trigger the GFCI, my electric shaver does that to the GFCI breaker in the bathroom, it is one of two on the same circuit but only the one with the shaver goes off when shaver is turned off...just reset the GFCI, and hell with it....

Obviously referring to the main power switch on the Variac.....now as to load, I dunno, not messed with that configuration.....I would be more tempted to put the GFCI on the output....but that depends on your use, and why you need either one.....
mrvette is offline   Reply With Quote
Old 07-10-2019, 7:13pm   #4
Black94lt1
Barn Stall Owner #13
Barn Raising II,III,IV

NCM Supporter '13,'14,'16,'17,'19,'20
Bantayan Kids '13,'15,'17
GTMS ‘18
Points: 24,779, Level: 100
Activity: 5.0%
 
Black94lt1's Avatar
 
Join Date: Jan 2012
Location: Ypsilanti, Mi
Posts: 13,262
Thanks: 7,760
Thanked 2,637 Times in 1,952 Posts
Gameroom Barn Bucks: $425244
Default

Quote:
Originally Posted by ZipZap View Post
I'm assuming this is a non-isolated VAT. Could you run an isolation transformer upstream and then use a GFCI?

Or, are you trying to GFCI the output?
If I understand correctly, that is one of the questions I have, is there a difference between putting a GFCI outlet for the output or using an GFCI breaker on the 120 side
Black94lt1 is offline   Reply With Quote
Old 07-10-2019, 7:16pm   #5
Black94lt1
Barn Stall Owner #13
Barn Raising II,III,IV

NCM Supporter '13,'14,'16,'17,'19,'20
Bantayan Kids '13,'15,'17
GTMS ‘18
Points: 24,779, Level: 100
Activity: 5.0%
 
Black94lt1's Avatar
 
Join Date: Jan 2012
Location: Ypsilanti, Mi
Posts: 13,262
Thanks: 7,760
Thanked 2,637 Times in 1,952 Posts
Gameroom Barn Bucks: $425244
Default

Quote:
Originally Posted by mrvette View Post
Any properly wired Variac should not upset a decent GFCI breaker.....

now, turning it on/off with a power switch MAY trigger the GFCI, my electric shaver does that to the GFCI breaker in the bathroom, it is one of two on the same circuit but only the one with the shaver goes off when shaver is turned off...just reset the GFCI, and hell with it....

Obviously referring to the main power switch on the Variac.....now as to load, I dunno, not messed with that configuration.....I would be more tempted to put the GFCI on the output....but that depends on your use, and why you need either one.....
One issue is these often run 24 hours/day with no one around, so tripping a GFCI will result in lost production if no one is around. If it only happens when turned on or off, that can be managed but if it trips the GFCI at random times, that’s a no go
Black94lt1 is offline   Reply With Quote
Old 07-10-2019, 8:23pm   #6
ZipZap
Barn Stall Owner #55
Island14 Cardio Team
Points: 61,734, Level: 100
Activity: 94.2%
 
ZipZap's Avatar
 
Join Date: Jan 2011
Location: A sympathetic, well-meaning, elderly man with a poor memory
Posts: 14,514
Thanks: 3,700
Thanked 9,066 Times in 4,289 Posts
Gameroom Barn Bucks: $23236
Default

Quote:
Originally Posted by Black94lt1 View Post
If I understand correctly, that is one of the questions I have, is there a difference between putting a GFCI outlet for the output or using an GFCI breaker on the 120 side
I think the biggest difference is that a normal GFCI will not work very well below the rated voltage, so being on the output might be problematic.

I would think a decent isolation transformer would get rid of the fluctuations driven by the load in the VAT draw. So 1/1 isolation transformer on the line, and then the VAT plugged into that.

If everything is grounded properly the GFCI should still serve as protection, even if the problem occurs in the ultimate load, as the imbalance will show up back at the outlet.
ZipZap is online now   Reply With Quote
Old 07-10-2019, 8:32pm   #7
ZipZap
Barn Stall Owner #55
Island14 Cardio Team
Points: 61,734, Level: 100
Activity: 94.2%
 
ZipZap's Avatar
 
Join Date: Jan 2011
Location: A sympathetic, well-meaning, elderly man with a poor memory
Posts: 14,514
Thanks: 3,700
Thanked 9,066 Times in 4,289 Posts
Gameroom Barn Bucks: $23236
Default

Quote:
Originally Posted by mrvette View Post
Any properly wired Variac should not upset a decent GFCI breaker.....

now, turning it on/off with a power switch MAY trigger the GFCI, my electric shaver does that to the GFCI breaker in the bathroom, it is one of two on the same circuit but only the one with the shaver goes off when shaver is turned off...just reset the GFCI, and hell with it....

Obviously referring to the main power switch on the Variac.....now as to load, I dunno, not messed with that configuration.....I would be more tempted to put the GFCI on the output....but that depends on your use, and why you need either one.....
I would agree that a VAT powering a stable load should be fine, but if the load is changing, the single coil characteristic of the VAT will definitely cause imbalances on the input power that could trip the GFCI.
ZipZap is online now   Reply With Quote
Old 07-11-2019, 2:29am   #8
Black94lt1
Barn Stall Owner #13
Barn Raising II,III,IV

NCM Supporter '13,'14,'16,'17,'19,'20
Bantayan Kids '13,'15,'17
GTMS ‘18
Points: 24,779, Level: 100
Activity: 5.0%
 
Black94lt1's Avatar
 
Join Date: Jan 2012
Location: Ypsilanti, Mi
Posts: 13,262
Thanks: 7,760
Thanked 2,637 Times in 1,952 Posts
Gameroom Barn Bucks: $425244
Default

Quote:
Originally Posted by ZipZap View Post
I think the biggest difference is that a normal GFCI will not work very well below the rated voltage, so being on the output might be problematic.

I would think a decent isolation transformer would get rid of the fluctuations driven by the load in the VAT draw. So 1/1 isolation transformer on the line, and then the VAT plugged into that.

If everything is grounded properly the GFCI should still serve as protection, even if the problem occurs in the ultimate load, as the imbalance will show up back at the outlet.
Quote:
Originally Posted by ZipZap View Post
I would agree that a VAT powering a stable load should be fine, but if the load is changing, the single coil characteristic of the VAT will definitely cause imbalances on the input power that could trip the GFCI.
Thank you, it sounds like it may be fine but it may be time to set up a test location by changing to a GFCI breaker and seeing if it is stable or trips
Black94lt1 is offline   Reply With Quote
Old 07-11-2019, 3:34am   #9
mrvette
Latin American Goat Roper
Barn Stall Owner #101
Bantayan Kids '13
Points: 132,054, Level: 100
Activity: 12.9%
 
mrvette's Avatar
 
Join Date: Nov 2009
Location: Orange Park Florida
Posts: 60,529
Thanks: 32,757
Thanked 11,510 Times in 5,682 Posts
Gameroom Barn Bucks: $1138393
Default

So, to get this straight, you are in an industrial application here, and some code or other demands you have a GFI breaker on this appliance.....why?? what it doing? reducing voltage to some heater dealing with water??
mrvette is offline   Reply With Quote
Old 07-11-2019, 6:08am   #10
Black94lt1
Barn Stall Owner #13
Barn Raising II,III,IV

NCM Supporter '13,'14,'16,'17,'19,'20
Bantayan Kids '13,'15,'17
GTMS ‘18
Points: 24,779, Level: 100
Activity: 5.0%
 
Black94lt1's Avatar
 
Join Date: Jan 2012
Location: Ypsilanti, Mi
Posts: 13,262
Thanks: 7,760
Thanked 2,637 Times in 1,952 Posts
Gameroom Barn Bucks: $425244
Default

Quote:
Originally Posted by mrvette View Post
So, to get this straight, you are in an industrial application here, and some code or other demands you have a GFI breaker on this appliance.....why?? what it doing? reducing voltage to some heater dealing with water??
Wet chemistry labs, these are on fume hoods to supply variable power to research equipment. Safety staff who don’t understand all the nuances of reality are citing it as deficient as they are within 6’ of water. I agree that that would normally dictate GFCI but I’m trying to determine why they were not set up that way to begin with, and were approved by the electrical inspector
Black94lt1 is offline   Reply With Quote
Old 07-11-2019, 7:36am   #11
mrvette
Latin American Goat Roper
Barn Stall Owner #101
Bantayan Kids '13
Points: 132,054, Level: 100
Activity: 12.9%
 
mrvette's Avatar
 
Join Date: Nov 2009
Location: Orange Park Florida
Posts: 60,529
Thanks: 32,757
Thanked 11,510 Times in 5,682 Posts
Gameroom Barn Bucks: $1138393
Default

Quote:
Originally Posted by Black94lt1 View Post
Wet chemistry labs, these are on fume hoods to supply variable power to research equipment. Safety staff who don’t understand all the nuances of reality are citing it as deficient as they are within 6’ of water. I agree that that would normally dictate GFCI but I’m trying to determine why they were not set up that way to begin with, and were approved by the electrical inspector
Well, I bet these two thought have crossed your mind already....one is that the plant/wiring/setup predates the invention of GFCI by some years....so in fact is grandfathered in??

I think that if the load it fairly steady on the Variac, there should be no trouble running off a typical household GCFI, now it it's a switched load coming on/off all the time....all bets are off.....especially if it's an inductive load taking something like ten amps.....the kick on/off by the switch will throw the breaker almost for sure, if my silly little shaver can induce enough kick to toss the breaker, that Variac good for 15-20 amps sure as hell will....

You know, I forgot, how about a surge supressor power strip plugged into the GFCI and then to the Variac, AND maybe one into the variac output to the load plugged into the strip.......

gotta kill that surge somehow.....that's watt she said.....
mrvette is offline   Reply With Quote
Old 07-11-2019, 8:56pm   #12
Black94lt1
Barn Stall Owner #13
Barn Raising II,III,IV

NCM Supporter '13,'14,'16,'17,'19,'20
Bantayan Kids '13,'15,'17
GTMS ‘18
Points: 24,779, Level: 100
Activity: 5.0%
 
Black94lt1's Avatar
 
Join Date: Jan 2012
Location: Ypsilanti, Mi
Posts: 13,262
Thanks: 7,760
Thanked 2,637 Times in 1,952 Posts
Gameroom Barn Bucks: $425244
Default

Quote:
Originally Posted by mrvette View Post
Well, I bet these two thought have crossed your mind already....one is that the plant/wiring/setup predates the invention of GFCI by some years....so in fact is grandfathered in??
2004 build, ~$100 million, no expenses spared, problem now is we have limited documentation as not everything stayed with the facility when it was sold. Knowing it was inspected leads me to believe there is a reason why it was not GFCI, I just don’t have those records
Black94lt1 is offline   Reply With Quote
Reply

The Vette Barn > Off Topic/Babes/Other > Off Topic


Thread Tools Search this Thread
Search this Thread:

Advanced Search

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 11:16pm.


Powered by vBulletin® Version 3.8.4
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
User Alert System provided by Advanced User Tagging (Pro) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.
Copyright © 2009 - 2024 The Vette Barn


Support the Barn:
 
Download the Mobile App;
 
Follow us on Facebook:

Become a Stall Owner

 

Apple iOS App        Google Android App

 

Visit our Facebook page