Quote:
Originally Posted by BayouCountry View Post
Replace breaker if resetting service power switch doesn't work.

What happens if you reset the air handler breaker after turning off heat?
What happens if you reset the outside service switch after turning off the heat?

You didn't mention if the condenser has a heat pump.

No heat pump. No issue during heat or switch from AC to heat. Only heat to AC. For AC to heat, all I do is set the thermostat to heat and set the temp. If I do this going from heat to AC, the t-stat kicks the inside blower on, but the outside unit breaker trips. If I try to reset the breaker with the unit on AC and blower running, it will never reset. I have to turn the t-stat to "off", reset the breaker, then go back to the t-stat, set to "cool"and set the temp.