Started demo in the shop today, taking out wiring and conduit as it is not where I need it long term. All circuits connected to 20A breakers. Got 1/2 the wiring pulled out so far....and it's all 14awg. Bzzzt. That's correct for 15A breakers. :slap:

So I can reuse the conduit, but not the wires. Crap.

theriver
04-25-2011, 10:40pm
Started demo in the shop today, taking out wiring and conduit as it is not where I need it long term. All circuits connected to 20A breakers. Got 1/2 the wiring pulled out so far....and it's all 14awg. Bzzzt. That's correct for 15A breakers. :slap:

So I can reuse the conduit, but not the wires. Crap.

whatever your budget is now for copper you can double it :banghead:

kingpin
04-25-2011, 10:51pm
Eh you'll be fine...go ahead and reuse the 14 gauge stuff! :leaving:

DAB
04-25-2011, 10:55pm
whatever your budget is now for copper you can double it :banghead:

priced it out last week: $70 for 500 feet....black, white, green...$210 at least....ouch.

i have a mess of 14awg for cheap!

DJ_Critterus
04-25-2011, 11:20pm
As long as the conduit isn't damage I don't see why there's a problem. Wow.... Maybe Lars has a use after all. Can you answer this? :D

DAB
04-25-2011, 11:24pm
As long as the conduit isn't damage I don't see why there's a problem. Wow.... Maybe Lars has a use after all. Can you answer this? :D

The conduit is fine. The old wiring is undersized for the breakers.

theriver
04-25-2011, 11:36pm
i'd want 12 awg for a shop, too